Hot!1800W petrol generator hard to restart if hot

Author
rgormley
New Member
  • Total Posts : 2
  • Scores: 0
  • Reward points: 0
  • Joined: 2024/03/15 05:31:40
  • Status: offline
2024/03/15 05:57:20 (permalink)
0

1800W petrol generator hard to restart if hot

got hold of a generator from work (was sitting for 5 years) with about 20 hours on it
stripped it down, cleaned, checked it over.  all the usual stuff
head off checked OK, valves cleaned, re-seated, carby cleaned (ultrasonic cleaner) valve backlash set
anyway put it all together stuck some fuel it and it went on 2 pulls....happpy!! choke on for a second then flipped to run.
loaded with 1200 electric blow heater and it works fine.
 
BUT what i have noticed if it`s been running for 10 seconds or 2 mins, 10 mins (any run period)
if i turn it off and try to restart straight away it will NOT restart unless it`s pulled 50 to 100 times!! (i lost count)
 
if i leave it for and hour or 2 it will go 1st or 2nd pull  (choke on for a second then flipped to run) works OK
 
so whats with it being VERY! hard restart when it`s hot.(or even just warm)
 
tried full choke, half choke, no choke makes no difference.... just wont restart unless pulled MANY times
 
maybe when the electrical kill switch is turned off,  the motor will run down and is still puling fuel in (but not being burnt) and thus is flooding, hence VERY hard to re-start?
 
-got the correct oil and correct level
-machine is on level ground
- have tried disconnecting the low oil switch (no difference)
-checked valve clearance (when cold) and they are still spot on.
 
any ideas?
also whats with small silver thing on the side of the engine (above the low oil switch) with a black and yellow wire coming from it?
 
Cheers,
Richard

Attached Image(s)

4 Replies Related Threads

    SRTsFZ6
    Super Member
    • Total Posts : 2031
    • Scores: 74
    • Reward points: 0
    • Joined: 2018/11/18 07:20:58
    • Status: offline
    Re: 1800W petrol generator hard to restart if hot 2024/03/15 07:58:35 (permalink)
    0
    Check for spark when it's acting up.  Advise.
     
    Re the 3 wire doo dad, perhaps a temp sensor? 
    Try unbolting from the engine block but keep plugged in.
    If no change, try un-plugging it.
     
    Your issue sounds as if your loosing spark.
     
    .
    post edited by SRTsFZ6 - 2024/03/15 08:07:05

    Scott
    jerrydexture
    New Member
    • Total Posts : 4
    • Scores: 0
    • Reward points: 0
    • Joined: 2024/02/29 05:06:18
    • Status: offline
    Re: 1800W petrol generator hard to restart if hot 2024/03/15 15:55:22 (permalink)
    0
    Great job on getting your hands on that generator and giving it some TLC! It sounds like you've done a thorough job cleaning and checking everything, which paid off with a smooth start-up on just two pulls - impressive!
    As for the hot restart issue, it sounds like it might be related to fuel flooding when the engine is warm. One possibility could be that the engine is still pulling in fuel even after the electrical kill switch is turned off, leading to flooding and making it difficult to restart.
    You've already tried various choke settings with no luck, and you've ruled out issues like incorrect oil level and valve clearance. Have you checked the carburetor settings and ensured they're adjusted properly for hot starts?
    Regarding the small silver thing on the side of the engine with the black and yellow wires, it sounds like it could be a component related to engine safety features, possibly an ignition module or some form of sensor.
    Keep troubleshooting, and hopefully, you'll find a solution soon!
    post edited by Mikel1 - 2024/03/16 09:34:58
    rgormley
    New Member
    • Total Posts : 2
    • Scores: 0
    • Reward points: 0
    • Joined: 2024/03/15 05:31:40
    • Status: offline
    Re: 1800W petrol generator hard to restart if hot 2024/03/19 05:13:29 (permalink)
    0
    SRTsFZ6
    Check for spark when it's acting up.  Advise.
     
    Re the 3 wire doo dad, perhaps a temp sensor? 
    Try unbolting from the engine block but keep plugged in.
    If no change, try un-plugging it.
     
    Your issue sounds as if your loosing spark.
     
    .


    ok i bit the bullet and bought a new ignition coil.
    genny now works like a charm!! cold or hot, 1 -2 pulls repeatable...
    Yay!
    i still don`t know what the other 2 wire thingo is, does not seem to make a difference if connected or not?
     
     
     

    Attached Image(s)

    SRTsFZ6
    Super Member
    • Total Posts : 2031
    • Scores: 74
    • Reward points: 0
    • Joined: 2018/11/18 07:20:58
    • Status: offline
    Re: 1800W petrol generator hard to restart if hot 2024/03/21 07:25:16 (permalink)
    0
    Yep, coils can fail once they get hot, then spark comes back when cooled down...
     
    Glad you got it running!
     
    .

    Scott