I already know it was dumb :-[

I have a Westinghouse 7kw generator and crossed the jumper cables when attempting to start. All's now quiet and nothing even clicking?  Where do I start to find what I've fried?  Your help is greatly appreciated.

1 Reply Related Threads

    SRTsFZ6
    Super Member
    • Total Posts : 2031
    • Scores: 74
    • Reward points: 0
    • Joined: 2018/11/18 07:20:58
    • Status: offline
    Re: I already know it was dumb :-[ 2023/03/30 21:47:17 (permalink)
    0
    I would think there would be a fuse (or more) and at least a relay re-set button.
     
    If fuses are good, start tracing your 12 volts from the battery to the next point (likely starter relay or ignition switch) and so on...
     
    .
     